Consider a 400 V, 3-phase system. An industrial client is incurring penalties for a low power factor of 0.70 lagging. They are operating at 500 kW of real power. To avoid penalties, they need to improve the power factor to 0.95 lagging. What is the approximate reduction in line current (I_L) achieved by this power factor correction?

Initial apparent power (S1) = P / PF1 = 500 kW / 0.70 = 714.28 kVA. Initial line current (I_L1) = S1 / (√3 * V_L) = 714280 VA / (√3 * 400 V) = 1031 A. New appar

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: Consider a 400 V, 3-phase system. An industrial client is incurring penalties for a low power factor of 0.70 lagging. They are operating at 500 kW of real power. To avoid penalties, they need to improve the power factor to 0.95 lagging. What is the approximate reduction in line current (I_L) achieved by this power factor correction?

Answer options:

  • 150 A reduction
  • 220 A reduction ✅ 300 A reduction
  • 380 A reduction

Correct answer: 300 A reduction

Explanation: Initial apparent power (S1) = P / PF1 = 500 kW / 0.70 = 714.28 kVA. Initial line current (I_L1) = S1 / (√3 * V_L) = 714280 VA / (√3 * 400 V) = 1031 A. New apparent power (S2) = P / PF2 = 500 kW / 0.95 = 526.31 kVA. New line current (I_L2) = S2 / (√3 * V_L) = 526310 VA / (√3 * 400 V) = 759 A. The reduction in line current is I_L1 - I_L2 = 1031 A - 759 A = 272 A, which is approximately 300 A.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.