A transformer supplying a motor control centre is observed to be running significantly hotter than expected, even though the connected motors are not fully loaded. An electrician uses a power quality meter and finds a very low power factor. What is a direct consequence of this low power factor contributing to the transformer's overheating?
A low power factor means that the system is drawing more apparent power (kVA) for the same amount of real power (kW). This translates to higher current flow thr
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A transformer supplying a motor control centre is observed to be running significantly hotter than expected, even though the connected motors are not fully loaded. An electrician uses a power quality meter and finds a very low power factor. What is a direct consequence of this low power factor contributing to the transformer's overheating?
Answer options:
- The transformer's core is saturated.
- Increased magnetizing current.
- The transformer is operating at reduced kVA. ✅ Higher apparent power, leading to increased copper losses (I²R losses) in the windings.
Correct answer: Higher apparent power, leading to increased copper losses (I²R losses) in the windings.
Explanation: A low power factor means that the system is drawing more apparent power (kVA) for the same amount of real power (kW). This translates to higher current flow through the transformer windings than necessary for the useful work being done, leading to increased copper losses (I²R losses) and consequently, higher operating temperatures and potential overheating.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.