A technician is troubleshooting a 480 V, 60 Hz, three-phase motor with a nameplate rating of 50 horsepower (37.3 kW) that is consistently drawing more current than expected on two of its phases. An ammeter shows 75 A on phase A, 70 A on phase B, and 75 A on phase C. A power factor meter reads 0.68 lagging. What is the approximate reactive power (kVAR) being consumed by the motor?
First, calculate the average line current: (75 A + 70 A + 75 A) / 3 = 73.33 A. Then, calculate the apparent power (S) for the three-phase motor: S = √3 * V_L *
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A technician is troubleshooting a 480 V, 60 Hz, three-phase motor with a nameplate rating of 50 horsepower (37.3 kW) that is consistently drawing more current than expected on two of its phases. An ammeter shows 75 A on phase A, 70 A on phase B, and 75 A on phase C. A power factor meter reads 0.68 lagging. What is the approximate reactive power (kVAR) being consumed by the motor?
Answer options:
- 44.5 kVAR
- 58.8 kVAR ✅ 71.4 kVAR
- 87.6 kVAR
Correct answer: 71.4 kVAR
Explanation: First, calculate the average line current: (75 A + 70 A + 75 A) / 3 = 73.33 A. Then, calculate the apparent power (S) for the three-phase motor: S = √3 * V_L * I_L = √3 * 480 V * 73.33 A ≈ 60,950 VA or 60.95 kVA. Given the power factor (PF) of 0.68, calculate the reactive power (Q) using Q = S * sin(θ), where θ = arccos(PF). So, θ = arccos(0.68) ≈ 47.16 degrees. Then, Q = 60.95 kVA * sin(47.16°) ≈ 60.95 kVA * 0.733 ≈ 44.69 kVAR. Let's recheck the options and calculations. Ah, I made a calculation mistake; the nameplate horsepower and kW are distractors for the apparent power calculation. Let's recalculate carefully using correct steps. Average current Ia = (75+70+75)/3 = 73.33 A. Apparent power S = √3 * V_L * I_avg = 1.732 * 480 V * 73.33 A = 60946.3 VA = 60.95 kVA. Power Factor = 0.68. cos(ϴ) = 0.68 → ϴ = arccos(0.68) = 47.16 degrees. Reactive Power Q = S * sin(ϴ) = 60.95 kVA * sin(47.16°) = 60.95 * 0.7333 = 44.69 kVAR. This is closest to 44.5 kVAR. Option 2. My initial analysis led to C, let me re-evaluate one more time. The option C is 71.4 kVAR. How can this be derived? Perhaps a direct use of V and I. Let's simplify. If I use only 75A current without averaging. S = √3 * 480 * 75 = 62,353 VA = 62.35 kVA. Then Q = 62.35 * sin(47.16) = 62.35 * 0.733 = 45.7 kVAR. Still not 71.4 kVAR. Let's re-examine the question's premise where I might have miscalculated for the given answer. Let's assume the correct answer is indeed 71.4 kVAR from some reasoning for option C. If Q = 71.4 kVAR, and PF = 0.68. Then S * sin(ϴ) = 71.4. And S * cos(ϴ) = P. tan(ϴ) = Q/P. Arccos(0.68) = 47.16 degrees. sin(47.16) = 0.733. So S = Q / sin(ϴ) = 71.4 / 0.733 = 97.4 kVA. If S = 97.4 kVA, then V_L * I_L * √3 = 97400. 480 * I * √3 = 97400. I = 97400 / (480 * √3) = 97400 / 831.36 = 117.15 A. Avg current from the question was 73.33A. If the answer is C, there must be a mistake in the question, or my understanding of how current should be calculated for given phases. 'More current than expected on two of its phases' and then specific current values. This suggests a motor with some imbalance. For calculating total power, usually, the average current is used. The initial calculation (44.69 kVAR) leads to option A (44.5 kVAR). Given my previous issue with numerical accuracy in questions: I need to ensure my calculation aligns with one options. Re-calculating: S = √3 × V_L × I_L_avg = 1.732 × 480 V × 73.33 A ≈ 60.95 kVA. Power factor (PF) = 0.68, so cos(θ) = 0.68. sin(θ) = √(1 - PF^2) = √(1 - 0.68^2) = √(1 - 0.4624) = √(0.5376) ≈ 0.7332. Reactive Power (Q) = S × sin(θ) = 60.95 kVA × 0.7332 ≈ 44.69 kVAR. This is closest to 44.5 kVAR (Option A). I assume my previous selection was incorrect and was based on a prior error or a faulty assumption about the options. The correct answer should be 44.5 kVAR based on my recalculation.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.