A residential customer complains of dimming lights and warm panel breakers, despite not adding new large loads. An electrician checks the service and finds the total active power is 15 kW and the apparent power is 20 kVA. What is the power factor at the service entrance?

Power factor (PF) is the ratio of active power (P) to apparent power (S). So, PF = P / S. Given P = 15 kW and S = 20 kVA, PF = 15 kW / 20 kVA = 0.75. The sympto

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A residential customer complains of dimming lights and warm panel breakers, despite not adding new large loads. An electrician checks the service and finds the total active power is 15 kW and the apparent power is 20 kVA. What is the power factor at the service entrance?

Answer options:

  • 0.65 lagging ✅ 0.75 lagging
  • 0.85 lagging
  • 0.95 lagging

Correct answer: 0.75 lagging

Explanation: Power factor (PF) is the ratio of active power (P) to apparent power (S). So, PF = P / S. Given P = 15 kW and S = 20 kVA, PF = 15 kW / 20 kVA = 0.75. The symptoms of dimming lights and warm breakers without new loads suggest a low power factor, leading to higher reactive current and thus higher total current for the same active power.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.