An electrician is tasked with improving the power factor of a 100 kW, 480 V, three-phase load that currently has a power factor of 0.70 lagging. The goal is to raise the power factor to 0.95 lagging. What is the approximate reactive power (kVAR) that needs to be compensated by capacitors?

First, calculate the initial reactive power (Q1) for PF1 = 0.70. cos(θ1) = 0.70 → θ1 = 45.57°. Q1 = P * tan(θ1) = 100 kW * tan(45.57°) ≈ 100 kW * 1.020 = 102.0

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is tasked with improving the power factor of a 100 kW, 480 V, three-phase load that currently has a power factor of 0.70 lagging. The goal is to raise the power factor to 0.95 lagging. What is the approximate reactive power (kVAR) that needs to be compensated by capacitors?

Answer options:

  • 36 kVAR
  • 52 kVAR ✅ 71 kVAR
  • 94 kVAR

Correct answer: 71 kVAR

Explanation: First, calculate the initial reactive power (Q1) for PF1 = 0.70. cos(θ1) = 0.70 → θ1 = 45.57°. Q1 = P * tan(θ1) = 100 kW * tan(45.57°) ≈ 100 kW * 1.020 = 102.0 kVAR. Next, calculate the final reactive power (Q2) for PF2 = 0.95. cos(θ2) = 0.95 → θ2 = 18.19°. Q2 = P * tan(θ2) = 100 kW * tan(18.19°) ≈ 100 kW * 0.328 = 32.8 kVAR. The required compensation is Q_c = Q1 - Q2 = 102.0 kVAR - 32.8 kVAR = 69.2 kVAR. The closest option is 71 kVAR.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.