A three-phase, 600 V motor is experiencing frequent overcurrent trips, but measurements show the motor draw is within its full load ampere (FLA) rating. Upon further investigation, the electrician discovers unbalanced phase voltages, with one phase measuring 580 V, another 605 V, and the third 610 V. What is the approximate voltage unbalance percentage?
To calculate voltage unbalance: 1. Find the average voltage: (580 V + 605 V + 610 V) / 3 = 598.33 V. 2. Find the maximum deviation from the average: 598.33 V -
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A three-phase, 600 V motor is experiencing frequent overcurrent trips, but measurements show the motor draw is within its full load ampere (FLA) rating. Upon further investigation, the electrician discovers unbalanced phase voltages, with one phase measuring 580 V, another 605 V, and the third 610 V. What is the approximate voltage unbalance percentage?
Answer options:
- 1.2%
- 2.5% ✅ 3.4%
- 4.1%
Correct answer: 3.4%
Explanation: To calculate voltage unbalance: 1. Find the average voltage: (580 V + 605 V + 610 V) / 3 = 598.33 V. 2. Find the maximum deviation from the average: 598.33 V - 580 V = 18.33 V. 3. Calculate the percentage: (18.33 V / 598.33 V) * 100% ≈ 3.06%. While 3.06% is the closest, options are simplified. However, for voltage unbalance, many standards define the nominal voltage as the reference. Using the nominal voltage (600V), (600 - 580) / 600 = 3.33%. 3.4% is the closest answer. IEEE C57.110 recommends that voltage unbalance should not exceed 2%.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.