Electrician Red Seal · Question
A three-phase, 600 V (line-to-line) delta-connected motor is drawing 10 A per phase. What is the approximate total power (in kW) consumed by the motor if its power factor is 0.85 and it has an efficiency of 90%?
For a delta-connected motor, the line current is root-3 times the phase current. However, power calculation uses line values or phase values consistently. Total
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A three-phase, 600 V (line-to-line) delta-connected motor is drawing 10 A per phase. What is the approximate total power (in kW) consumed by the motor if its power factor is 0.85 and it has an efficiency of 90%?
Answer options:
- 8.8 kW
- 7.5 kW ✅ 8.3 kW
- 9.8 kW
Correct answer: 8.3 kW
Explanation: For a delta-connected motor, the line current is root-3 times the phase current. However, power calculation uses line values or phase values consistently. Total Apparent Power (S) = Root(3) * V_line * I_line. For a delta connection, I_line = Root(3) * I_phase. So, S = Root(3) * 600V * (Root(3) * 10A) = 3 * 600V * 10A = 18 kVA. Alternatively, using phase values, S = 3 * V_phase * I_phase. In delta, V_phase = V_line = 600V, so S = 3 * 600V * 10A = 18 kVA. Real Power (P) = S * Power Factor = 18 kVA * 0.85 = 15.3 kW. Since the question asks for power consumed by the motor, which implies input power, the efficiency is not applied to this calculation. The motor consumes 15.3 kW, but this option isn't available, suggesting a misinterpretation of 'per phase'. If '10 A per phase' refers to the line current (I_line = 10A), then P = Root(3) * V_line * I_line * PF = Root(3) * 600V * 10A * 0.85 = 1.732 * 600 * 10 * 0.85 = 8820 W or 8.82 kW. Checking the available options, 8.8 kW is the closest, meaning '10 A per phase' was intended as line current. Efficiency is applied to calculate output mechanical power, not input electrical power.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.