An industrial facility uses a power factor correction capacitor bank. Before installation, the load was 500 kVA at 0.75 lagging power factor. After installing the capacitors, the power factor improved to 0.95 lagging. What was the approximate reactive power (in kVAR) supplied by the capacitor bank?
First, calculate the real power (P) and initial reactive power (Q1). P = S1 * PF1 = 500 kVA * 0.75 = 375 kW. Q1 = sqrt(S1^2 - P^2) = sqrt(500^2 - 375^2) = sqrt(
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An industrial facility uses a power factor correction capacitor bank. Before installation, the load was 500 kVA at 0.75 lagging power factor. After installing the capacitors, the power factor improved to 0.95 lagging. What was the approximate reactive power (in kVAR) supplied by the capacitor bank?
Answer options:
- 150 kVAR ✅ 216 kVAR
- 185 kVAR
- 250 kVAR
Correct answer: 216 kVAR
Explanation: First, calculate the real power (P) and initial reactive power (Q1). P = S1 * PF1 = 500 kVA * 0.75 = 375 kW. Q1 = sqrt(S1^2 - P^2) = sqrt(500^2 - 375^2) = sqrt(250000 - 140625) = sqrt(109375) = 330.7 kVAR. Now, calculate the new reactive power (Q2) with the improved power factor. Since real power (P) does not change, S2 = P / PF2 = 375 kW / 0.95 = 394.7 kVA. Q2 = sqrt(S2^2 - P^2) = sqrt(394.7^2 - 375^2) = sqrt(155788 - 140625) = sqrt(15163) = 123.1 kVAR. The reactive power supplied by the capacitor bank (Qc) = Q1 - Q2 = 330.7 kVAR - 123.1 kVAR = 207.6 kVAR. The closest option is 216 kVAR. (A slight discrepancy exists if using tan(theta) method: Q1 = P * tan(acos(PF1)) = 375 * tan(acos(0.75)) = 375 * tan(41.41) = 375 * 0.8819 = 330.7 kVAR. Q2 = P * tan(acos(PF2)) = 375 * tan(acos(0.95)) = 375 * tan(18.19) = 375 * 0.3287 = 123.2 kVAR. Qc = 330.7 - 123.2 = 207.5 kVAR.) Rounding results in 208 kVAR, making 216 kVAR the nearest practical answer.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.