A three-phase, 600 V (line-to-line), 60 Hz electrical service supplies an industrial facility. If a technician measures the voltage between one phase conductor and the grounded (neutral) conductor, what approximate value would they expect to read?

For a 600 V, three-phase system, the phase-to-neutral voltage is calculated as the line-to-line voltage divided by the square root of 3 (600 V / √3 ≈ 347 V). Th

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A three-phase, 600 V (line-to-line), 60 Hz electrical service supplies an industrial facility. If a technician measures the voltage between one phase conductor and the grounded (neutral) conductor, what approximate value would they expect to read?

Answer options: ✅ 347 V

  • 208 V
  • 120 V
  • 600 V

Correct answer: 347 V

Explanation: For a 600 V, three-phase system, the phase-to-neutral voltage is calculated as the line-to-line voltage divided by the square root of 3 (600 V / √3 ≈ 347 V). This is a common voltage for lighting and smaller loads in industrial settings.