Electrician Red Seal · Question
A newly installed 120/208 V, three-phase, four-wire Wye service for a commercial building includes several non-linear loads (e.g., LED lighting with switch-mode power supplies, variable frequency drives). The electrician routinely measures current and finds excessive current (approaching 150% of rated phase current) flowing in the neutral conductor, even when phase currents are balanced. What is the primary cause of this anomalous neutral current?
In a balanced linear three-phase system, the fundamental currents cancel in the neutral. However, non-linear loads generate harmonic currents, especially odd tr
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A newly installed 120/208 V, three-phase, four-wire Wye service for a commercial building includes several non-linear loads (e.g., LED lighting with switch-mode power supplies, variable frequency drives). The electrician routinely measures current and finds excessive current (approaching 150% of rated phase current) flowing in the neutral conductor, even when phase currents are balanced. What is the primary cause of this anomalous neutral current?
Answer options:
- An intentional ground fault occurring at the service entrance.
- Reversed phase rotation causing a negative sequence current. ✅ High harmonic currents, particularly third harmonics, not cancelling in the neutral.
- Improper bonding between the main service panel and the building's metallic piping.
Correct answer: High harmonic currents, particularly third harmonics, not cancelling in the neutral.
Explanation: In a balanced linear three-phase system, the fundamental currents cancel in the neutral. However, non-linear loads generate harmonic currents, especially odd triplen harmonics (3rd, 9th, 15th, etc.). These triplen harmonics are in-phase in the neutral conductor of a Wye system and add up rather than cancel, leading to significant and potentially overheating neutral currents, even with balanced phase currents.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.