Electrician Red Seal · Question
After installing a new 480 V, 30 kVA, three-phase dry-type transformer, a journeyperson performs a turns ratio test using a TTR (Transformer Turns Ratio) meter. For a transformer with a primary voltage of 480 V and a secondary voltage of 208Y/120 V, what approximate turns ratio should they expect to measure between the H1-H2 terminals and the X1-X2 (phase-to-phase) secondary terminals?
The nominal turns ratio is calculated by dividing the primary phase voltage by the secondary phase voltage. For a 480 V delta primary and 208 V wye secondary, w
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: After installing a new 480 V, 30 kVA, three-phase dry-type transformer, a journeyperson performs a turns ratio test using a TTR (Transformer Turns Ratio) meter. For a transformer with a primary voltage of 480 V and a secondary voltage of 208Y/120 V, what approximate turns ratio should they expect to measure between the H1-H2 terminals and the X1-X2 (phase-to-phase) secondary terminals?
Answer options: ✅ 2.31:1
- 1.73:1
- 4.00:1
- 1.15:1
Correct answer: 2.31:1
Explanation: The nominal turns ratio is calculated by dividing the primary phase voltage by the secondary phase voltage. For a 480 V delta primary and 208 V wye secondary, we compare 480 V from line-to-line on the primary to 208 V line-to-line on the secondary. So, 480 V / 208 V = 2.3076, which is approximately 2.31:1. The TTR meter measures this ratio directly.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.