After installing a new 480 V, 30 kVA, three-phase dry-type transformer, a journeyperson performs a turns ratio test using a TTR (Transformer Turns Ratio) meter. For a transformer with a primary voltage of 480 V and a secondary voltage of 208Y/120 V, what approximate turns ratio should they expect to measure between the H1-H2 terminals and the X1-X2 (phase-to-phase) secondary terminals?

The nominal turns ratio is calculated by dividing the primary phase voltage by the secondary phase voltage. For a 480 V delta primary and 208 V wye secondary, w

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: After installing a new 480 V, 30 kVA, three-phase dry-type transformer, a journeyperson performs a turns ratio test using a TTR (Transformer Turns Ratio) meter. For a transformer with a primary voltage of 480 V and a secondary voltage of 208Y/120 V, what approximate turns ratio should they expect to measure between the H1-H2 terminals and the X1-X2 (phase-to-phase) secondary terminals?

Answer options: ✅ 2.31:1

  • 1.73:1
  • 4.00:1
  • 1.15:1

Correct answer: 2.31:1

Explanation: The nominal turns ratio is calculated by dividing the primary phase voltage by the secondary phase voltage. For a 480 V delta primary and 208 V wye secondary, we compare 480 V from line-to-line on the primary to 208 V line-to-line on the secondary. So, 480 V / 208 V = 2.3076, which is approximately 2.31:1. The TTR meter measures this ratio directly.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.