An electrician is checking a three-phase, 600 V motor using an insulation resistance tester (megohmmeter). With all three motor leads disconnected from the starter and isolated from each other and ground, the electrician tests between each lead and the motor frame. The readings are: Lead 1 to frame: 20 MΩ; Lead 2 to frame: >500 MΩ; Lead 3 to frame: 15 MΩ. What could these readings indicate?
Significant differences in insulation resistance readings between phases, especially values like 15 MΩ and 20 MΩ compared to >500 MΩ, suggest insulation degrada
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is checking a three-phase, 600 V motor using an insulation resistance tester (megohmmeter). With all three motor leads disconnected from the starter and isolated from each other and ground, the electrician tests between each lead and the motor frame. The readings are: Lead 1 to frame: 20 MΩ; Lead 2 to frame: >500 MΩ; Lead 3 to frame: 15 MΩ. What could these readings indicate?
Answer options:
- The motor has a winding-to-winding short.
- The motor is in excellent condition and ready for service. ✅ Lead 1 and Lead 3 likely have insulation degradation or contamination.
- The megohmmeter battery is low and needs replacement.
Correct answer: Lead 1 and Lead 3 likely have insulation degradation or contamination.
Explanation: Significant differences in insulation resistance readings between phases, especially values like 15 MΩ and 20 MΩ compared to >500 MΩ, suggest insulation degradation or surface contamination (e.g., dirt, moisture) on Lead 1 and Lead 3. A winding-to-winding short would be detected by testing between phases, not phase to ground. Excellent condition would show consistently high readings.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.