A three-phase, delta-wye connected transformer with a primary voltage of 600 V and a turns ratio of 10:1 (primary to secondary per phase) is supplying a balanced load. What is the approximate line-to-line secondary voltage?

For a delta-wye transformer, the line-to-line secondary voltage is the phase voltage multiplied by the square root of 3. With a 10:1 turns ratio, the phase volt

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A three-phase, delta-wye connected transformer with a primary voltage of 600 V and a turns ratio of 10:1 (primary to secondary per phase) is supplying a balanced load. What is the approximate line-to-line secondary voltage?

Answer options:

  • 34.7 V
  • 60 V ✅ 104 V
  • 208 V

Correct answer: 104 V

Explanation: For a delta-wye transformer, the line-to-line secondary voltage is the phase voltage multiplied by the square root of 3. With a 10:1 turns ratio, the phase voltage on the secondary is 600V / 10 = 60V. Therefore, the line-to-line secondary voltage is 60V * √3 ≈ 104V.