An electrician is commissioning a new three-phase 480 V delta primary to 208Y/120 V secondary transformer. After energizing the primary, the electrician measures the line-to-line secondary voltages and finds phase A-B at 208V, B-C at 208V, but C-A at 180V. What is the most likely cause of this discrepancy?
Uneven secondary voltages, specifically one phase significantly lower, are a classic symptom of an open circuit in one of the primary phases. A blown primary fu
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is commissioning a new three-phase 480 V delta primary to 208Y/120 V secondary transformer. After energizing the primary, the electrician measures the line-to-line secondary voltages and finds phase A-B at 208V, B-C at 208V, but C-A at 180V. What is the most likely cause of this discrepancy?
Answer options:
- The transformer is overloaded. ✅ One of the primary fuses for the transformer is blown.
- The transformer has an internal short circuit.
- Incorrect tap settings on the primary side.
Correct answer: One of the primary fuses for the transformer is blown.
Explanation: Uneven secondary voltages, specifically one phase significantly lower, are a classic symptom of an open circuit in one of the primary phases. A blown primary fuse would result in this condition, as it starves one leg of the delta primary, leading to an unbalanced magnetic field and uneven secondary voltages.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.