Electrician Red Seal · Question
According to the CEC, when a transformer is supplied from a feeder or branch circuit, and the transformer has a primary overcurrent device set at not more than 2.5 times the primary rated current (for circuit breakers) and the secondary conductors are protected by an overcurrent device, what is the maximum length of secondary conductor permissible without additional protection at the transformer secondary terminals?
CEC Rule 26-258(3)(c) allows for secondary conductors up to 7.5 m (25 ft) in length without individual overcurrent protection at the transformer secondary termi
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: According to the CEC, when a transformer is supplied from a feeder or branch circuit, and the transformer has a primary overcurrent device set at not more than 2.5 times the primary rated current (for circuit breakers) and the secondary conductors are protected by an overcurrent device, what is the maximum length of secondary conductor permissible without additional protection at the transformer secondary terminals?
Answer options:
- 1.5 m (5 ft)
- 3 m (10 ft) ✅ 7.5 m (25 ft)
- Not permitted; secondary conductors always require protection at the transformer terminals.
Correct answer: 7.5 m (25 ft)
Explanation: CEC Rule 26-258(3)(c) allows for secondary conductors up to 7.5 m (25 ft) in length without individual overcurrent protection at the transformer secondary terminals, provided the primary overcurrent device is rated no more than 2.5 times the primary rated current (for circuit breakers) and certain other conditions are met, including the secondary conductors terminating in a single overcurrent device or set of devices rated for the conductor's ampacity.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.