Electrician Red Seal · Question
An electrician is planning to parallel two single-phase transformers to increase capacity. Both transformers are 25 kVA, 600V primary to 120/240V secondary. Transformer A has a percent impedance of 3.5%, and Transformer B has a percent impedance of 4.0%. All other characteristics (voltage ratio, polarity, phase rotation) are identical. What issue is most likely to occur when paralleling these transformers with different impedances?
When transformers with different percent impedances are paralleled, the transformer with the lower impedance will attempt to supply a larger share of the load c
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is planning to parallel two single-phase transformers to increase capacity. Both transformers are 25 kVA, 600V primary to 120/240V secondary. Transformer A has a percent impedance of 3.5%, and Transformer B has a percent impedance of 4.0%. All other characteristics (voltage ratio, polarity, phase rotation) are identical. What issue is most likely to occur when paralleling these transformers with different impedances?
Answer options:
- Reduced overall efficiency of the parallel bank.
- An increase in secondary voltage due to circulating currents. ✅ Unbalanced load sharing, with the lower impedance transformer carrying a disproportionately higher share of the load.
- Increased voltage drop across the secondary terminals.
Correct answer: Unbalanced load sharing, with the lower impedance transformer carrying a disproportionately higher share of the load.
Explanation: When transformers with different percent impedances are paralleled, the transformer with the lower impedance will attempt to supply a larger share of the load current. This can lead to the lower impedance transformer becoming overloaded, even if the total load is within the combined kVA rating of both transformers.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.