Electrician Red Seal · Question
A 100 kVA, 600V delta primary to 208Y/120V secondary transformer is installed in a commercial building. The electrician notes that the primary feeders are protected by 125 A circuit breakers. What is the approximate full load current on the primary side of this transformer, and is the protection within typical CEC guidelines for this kVA rating?
The full load current (FLC) for a three-phase transformer primary is calculated as FLC = kVA * 1000 / (V_primary * √3). So, 100 kVA * 1000 / (600 V * √3) ≈ 1000
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 100 kVA, 600V delta primary to 208Y/120V secondary transformer is installed in a commercial building. The electrician notes that the primary feeders are protected by 125 A circuit breakers. What is the approximate full load current on the primary side of this transformer, and is the protection within typical CEC guidelines for this kVA rating?
Answer options:
- Primary FLC ≈ 96 A; Protection is too high. ✅ Primary FLC ≈ 96 A; Protection is within guidelines.
- Primary FLC ≈ 167 A; Protection is too low.
- Primary FLC ≈ 167 A; Protection is within guidelines.
Correct answer: Primary FLC ≈ 96 A; Protection is within guidelines.
Explanation: The full load current (FLC) for a three-phase transformer primary is calculated as FLC = kVA * 1000 / (V_primary * √3). So, 100 kVA * 1000 / (600 V * √3) ≈ 100000 / (600 * 1.732) ≈ 100000 / 1039.2 ≈ 96.2 A. According to CEC Rule 26-254(1)(a)(i), for a transformer with a rated primary current of 96.2 A, the overcurrent device shall not exceed 125% of the rated primary current without exceeding 250% where 125% is not a standard size. 96.2 A * 1.25 = 120.25 A. A 125 A breaker is the next standard size above 120.25 A and does not exceed 250% of the transformer's rated primary current (96.2 A * 2.5 = 240.5 A), so 125 A is within guidelines.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.