An electrician is running NMD90 (non-metallic sheathed cable) through bored holes in wooden studs. What is the minimum distance from the edge of the stud to the nearest edge of the bored hole, according to the CEC, if no protection plates are used?

Rule 12-516(1) of the CEC specifies that, where no protection plate is installed, the nearest edge of a bored hole through wooden members shall be not less than

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is running NMD90 (non-metallic sheathed cable) through bored holes in wooden studs. What is the minimum distance from the edge of the stud to the nearest edge of the bored hole, according to the CEC, if no protection plates are used?

Answer options:

  • 25 mm (1 inch) ✅ 32 mm (1 1/4 inches)
  • 19 mm (3/4 inch)
  • 12 mm (1/2 inch)

Correct answer: 32 mm (1 1/4 inches)

Explanation: Rule 12-516(1) of the CEC specifies that, where no protection plate is installed, the nearest edge of a bored hole through wooden members shall be not less than 32 mm (1 1/4 inches) from the nearest edge of the member. This ensures the cable is adequately protected from nails or screws.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.