Electrician Red Seal · Question
During an inspection, a journeyperson notes that a 20 A branch circuit supplying a lighting load in a suspended ceiling space of a commercial building is installed using open wiring methods. The conductors are 12 AWG T90 nylon, neatly run and strapped, but not enclosed in conduit or cable. Under what conditions is this wiring method generally NOT permitted in a commercial building according to the CEC?
CEC Rule 12-100 states that open wiring is not permitted in commercial, industrial, or institutional buildings, except in certain specific, usually temporary, a
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: During an inspection, a journeyperson notes that a 20 A branch circuit supplying a lighting load in a suspended ceiling space of a commercial building is installed using open wiring methods. The conductors are 12 AWG T90 nylon, neatly run and strapped, but not enclosed in conduit or cable. Under what conditions is this wiring method generally NOT permitted in a commercial building according to the CEC?
Answer options:
- When the conductors are copper
- When the ceiling space is not used as a plenum
- When the voltage is 120 V ✅ As a rule, open wiring is not permitted for branch circuits in commercial suspended ceiling spaces.
Correct answer: As a rule, open wiring is not permitted for branch circuits in commercial suspended ceiling spaces.
Explanation: CEC Rule 12-100 states that open wiring is not permitted in commercial, industrial, or institutional buildings, except in certain specific, usually temporary, agricultural, or exposed industrial applications. For typical branch circuits in commercial suspended ceiling spaces, enclosed wiring methods like EMT, AC90, or conduit systems are mandatory.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.