Electrician Red Seal · Question
An industrial electrician is asked to install a new control panel with several conduits entering from the bottom. The panel is located in a Class I, Division 2 hazardous location where flammable gases or vapours may be present in abnormal operating conditions. What specific CEC requirement must be met for the conduit entries to prevent the spread of gas into the panel or adjacent non-hazardous areas?
CEC Rule 18-102(3)(b) specifically requires that in Class I, Division 2 locations, a sealing fitting must be installed in each conduit run entering an enclosure
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An industrial electrician is asked to install a new control panel with several conduits entering from the bottom. The panel is located in a Class I, Division 2 hazardous location where flammable gases or vapours may be present in abnormal operating conditions. What specific CEC requirement must be met for the conduit entries to prevent the spread of gas into the panel or adjacent non-hazardous areas?
Answer options:
- All conduits must be sealed with a firestopping compound. ✅ A sealing fitting must be installed in each conduit entrance to the enclosure or within 450 mm (18 inches) of the enclosure.
- The conduits must be drained and vented to the atmosphere.
- Only liquidtight flexible metal conduit can be used for connections to the panel.
Correct answer: A sealing fitting must be installed in each conduit entrance to the enclosure or within 450 mm (18 inches) of the enclosure.
Explanation: CEC Rule 18-102(3)(b) specifically requires that in Class I, Division 2 locations, a sealing fitting must be installed in each conduit run entering an enclosure that contains arcing or high-temperature devices, or within 450 mm (18 inches) of such an enclosure, to prevent the passage of flammable gases or vapours.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.