Electrician Red Seal · Question
A journeyperson is installing a new 200 A, 600 V service entrance conductor in a commercial building. The conductors are aluminum and will be run in rigid PVC conduit underground. According to the Canadian Electrical Code (CEC), what is the minimum acceptable diameter for this conduit, assuming a standard 3-conductor plus neutral configuration and considering voltage drop will be addressed by up-sizing conductors if necessary?
For 200 A aluminum conductors (typically 250 kcmil or 300 kcmil depending on insulation and conditions) and a 3-conductor plus neutral configuration, a 103 mm (
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A journeyperson is installing a new 200 A, 600 V service entrance conductor in a commercial building. The conductors are aluminum and will be run in rigid PVC conduit underground. According to the Canadian Electrical Code (CEC), what is the minimum acceptable diameter for this conduit, assuming a standard 3-conductor plus neutral configuration and considering voltage drop will be addressed by up-sizing conductors if necessary?
Answer options:
- 63 mm (2 ½ in.)
- 78 mm (3 in.) ✅ 103 mm (4 in.)
- 129 mm (5 in.)
Correct answer: 103 mm (4 in.)
Explanation: For 200 A aluminum conductors (typically 250 kcmil or 300 kcmil depending on insulation and conditions) and a 3-conductor plus neutral configuration, a 103 mm (4 in.) rigid PVC conduit is generally required to meet conductor fill requirements, as per CEC Table 6 and Appendix B. Smaller conduits would exceed the allowable fill percentage.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.