An electrician is sizing overcurrent protection for a 15 kW, 208 V, 3-phase resistive heating load. The heaters are continuous duty. What is the minimum standard-rated circuit breaker size required, assuming the conductors are sized correctly for the load?

First, calculate the full-load current: I = P / (√3 × V) = 15000 W / (1.732 × 208 V) ≈ 41.6 A. For continuous loads, CEC Rule 8-104(2) requires overcurrent prot

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is sizing overcurrent protection for a 15 kW, 208 V, 3-phase resistive heating load. The heaters are continuous duty. What is the minimum standard-rated circuit breaker size required, assuming the conductors are sized correctly for the load?

Answer options:

  • 40 A ✅ 50 A
  • 60 A
  • 70 A

Correct answer: 50 A

Explanation: First, calculate the full-load current: I = P / (√3 × V) = 15000 W / (1.732 × 208 V) ≈ 41.6 A. For continuous loads, CEC Rule 8-104(2) requires overcurrent protection to be sized at 125% of the calculated current. So, 41.6 A × 1.25 = 52 A. The next standard fuse or circuit breaker size above 52 A is 50 A, as per CEC Rule 14-106(1) and Table 13.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.