An electrician is sizing overcurrent protection for a 15 kW, 208 V, 3-phase resistive heating load. The heaters are continuous duty. What is the minimum standard-rated circuit breaker size required, assuming the conductors are sized correctly for the load?
First, calculate the full-load current: I = P / (√3 × V) = 15000 W / (1.732 × 208 V) ≈ 41.6 A. For continuous loads, CEC Rule 8-104(2) requires overcurrent prot
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is sizing overcurrent protection for a 15 kW, 208 V, 3-phase resistive heating load. The heaters are continuous duty. What is the minimum standard-rated circuit breaker size required, assuming the conductors are sized correctly for the load?
Answer options:
- 40 A ✅ 50 A
- 60 A
- 70 A
Correct answer: 50 A
Explanation: First, calculate the full-load current: I = P / (√3 × V) = 15000 W / (1.732 × 208 V) ≈ 41.6 A. For continuous loads, CEC Rule 8-104(2) requires overcurrent protection to be sized at 125% of the calculated current. So, 41.6 A × 1.25 = 52 A. The next standard fuse or circuit breaker size above 52 A is 50 A, as per CEC Rule 14-106(1) and Table 13.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.