When installing electrical metallic tubing (EMT) in a dry, unfinished basement, what is the maximum permissible distance between supports for a 19 mm (3/4 in.) EMT conduit, according to CEC Table 18?
For EMT conduit not exceeding 21 mm (3/4 in.) nominal size, CEC Table 18 specifies a maximum distance between supports of 1.5 m (5 ft.). This ensures proper sup
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: When installing electrical metallic tubing (EMT) in a dry, unfinished basement, what is the maximum permissible distance between supports for a 19 mm (3/4 in.) EMT conduit, according to CEC Table 18?
Answer options:
- 1.0 m (3 ft. 3 in.) ✅ 1.5 m (5 ft.)
- 2.0 m (6 ft. 7 in.)
- 2.5 m (8 ft. 2 in.)
Correct answer: 1.5 m (5 ft.)
Explanation: For EMT conduit not exceeding 21 mm (3/4 in.) nominal size, CEC Table 18 specifies a maximum distance between supports of 1.5 m (5 ft.). This ensures proper support and prevents sagging or damage to the conduit.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.