An electrician is installing a new 240 V circuit for an electric vehicle charging station in a detached garage. The service to the detached garage is a 60 A, 120/240 V feeder. The charging station requires a continuous load of 32 A. What is the minimum allowable size for the copper conductors, assuming NMD90 cable and ambient temperature of 30°C?

For a continuous load of 32 A, the overcurrent device must be sized at 125% of the continuous load: 32 A * 1.25 = 40 A. Consulting Table 2 and Table 4 of the CE

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is installing a new 240 V circuit for an electric vehicle charging station in a detached garage. The service to the detached garage is a 60 A, 120/240 V feeder. The charging station requires a continuous load of 32 A. What is the minimum allowable size for the copper conductors, assuming NMD90 cable and ambient temperature of 30°C?

Answer options: ✅ 8 AWG

  • 10 AWG
  • 6 AWG
  • 12 AWG

Correct answer: 8 AWG

Explanation: For a continuous load of 32 A, the overcurrent device must be sized at 125% of the continuous load: 32 A * 1.25 = 40 A. Consulting Table 2 and Table 4 of the CEC, a 40 A breaker requires a minimum of 8 AWG copper wire (NMD90, 90°C column) to safely carry the current. 10 AWG is only rated for 35 A.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.