An electrician is installing a new 240 V circuit for an electric vehicle charging station in a detached garage. The service to the detached garage is a 60 A, 120/240 V feeder. The charging station requires a continuous load of 32 A. What is the minimum allowable size for the copper conductors, assuming NMD90 cable and ambient temperature of 30°C?
For a continuous load of 32 A, the overcurrent device must be sized at 125% of the continuous load: 32 A * 1.25 = 40 A. Consulting Table 2 and Table 4 of the CE
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An electrician is installing a new 240 V circuit for an electric vehicle charging station in a detached garage. The service to the detached garage is a 60 A, 120/240 V feeder. The charging station requires a continuous load of 32 A. What is the minimum allowable size for the copper conductors, assuming NMD90 cable and ambient temperature of 30°C?
Answer options: ✅ 8 AWG
- 10 AWG
- 6 AWG
- 12 AWG
Correct answer: 8 AWG
Explanation: For a continuous load of 32 A, the overcurrent device must be sized at 125% of the continuous load: 32 A * 1.25 = 40 A. Consulting Table 2 and Table 4 of the CEC, a 40 A breaker requires a minimum of 8 AWG copper wire (NMD90, 90°C column) to safely carry the current. 10 AWG is only rated for 35 A.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.