An electrician is troubleshooting a commercial kitchen circuit. A 3-phase, 208 V, 5 hp motor is connected. The motor's nameplate indicates a full load current (FLC) of 16.7 A. According to the Canadian Electrical Code, what is the minimum continuous current rating required for the branch circuit conductors supplying this motor?

When sizing conductors for a motor, Rule 28-106(1) of the CEC specifies that continuous current rating of the conductors shall be not less than the value of the

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An electrician is troubleshooting a commercial kitchen circuit. A 3-phase, 208 V, 5 hp motor is connected. The motor's nameplate indicates a full load current (FLC) of 16.7 A. According to the Canadian Electrical Code, what is the minimum continuous current rating required for the branch circuit conductors supplying this motor?

Answer options:

  • 20.9 A
  • 25.0 A ✅ 16.7 A
  • 29.2 A

Correct answer: 16.7 A

Explanation: When sizing conductors for a motor, Rule 28-106(1) of the CEC specifies that continuous current rating of the conductors shall be not less than the value of the full load current (FLC) obtained from Table 44 in the CEC. For a 5 hp, 208 V, 3-phase motor, Table 44 lists an FLC of 16.7 A. Therefore, the minimum continuous current rating required for the conductors is 16.7 A, not 125% of the nameplate value.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.