During the inspection of a new residential service installation, an electrical inspector notices that the main service disconnect is rated for 125 A, but the utility's overhead service conductors are rated for 150 A. The meter base is rated for 200 A. Is this installation compliant with the Canadian Electrical Code (CEC)?
Rule 8-106(1) of the CEC permits the rating of the service box or service disconnecting means to be not less than the calculated demand load, even if the servic
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: During the inspection of a new residential service installation, an electrical inspector notices that the main service disconnect is rated for 125 A, but the utility's overhead service conductors are rated for 150 A. The meter base is rated for 200 A. Is this installation compliant with the Canadian Electrical Code (CEC)?
Answer options: ✅ Yes, the service disconnect rating can be less than the utility conductors.
- No, the service disconnect must be rated for at least 150 A.
- Yes, as long as the meter base is rated higher than the disconnect.
- No, the service disconnect rating must match the meter base rating.
Correct answer: Yes, the service disconnect rating can be less than the utility conductors.
Explanation: Rule 8-106(1) of the CEC permits the rating of the service box or service disconnecting means to be not less than the calculated demand load, even if the service conductors or utility supply has a higher ampacity. It does not require a match to the utility conductor or meter base rating.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.