A journeyperson is installing a new submersible pump in a well. The pump motor nameplate indicates a full-load current of 12 A at 240 V. The circuit protection will be a circuit breaker. What is the MAXIMUM standard rating for the circuit breaker permitted by the Canadian Electrical Code (CEC) for motor branch circuits lacking specific overload protection in the breaker itself?
Rule 28-200(a) and Table 29 of the CEC allow for circuit breakers that do not have adjustable trips to be sized at 250% of the motor full-load current for a sin
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A journeyperson is installing a new submersible pump in a well. The pump motor nameplate indicates a full-load current of 12 A at 240 V. The circuit protection will be a circuit breaker. What is the MAXIMUM standard rating for the circuit breaker permitted by the Canadian Electrical Code (CEC) for motor branch circuits lacking specific overload protection in the breaker itself?
Answer options:
- 15 A
- 20 A ✅ 25 A
- 30 A
Correct answer: 25 A
Explanation: Rule 28-200(a) and Table 29 of the CEC allow for circuit breakers that do not have adjustable trips to be sized at 250% of the motor full-load current for a single-phase AC squirrel cage motor. 12 A x 250% = 30 A. However, Rule 28-202(1)(d) states that where the rating of the branch circuit overcurrent device is greater than 20 A, it must not exceed the maximum rating of supplementary overcurrent protection marked on the pump motor or controller. If not marked, a 25 A breaker is the next standard size down if 30 A exceeds other limitations, and 25 A is commonly used for a 12 A motor. For a 12A motor, a 25A breaker is the common and code-compliant choice by following the next standard size down from the calculated 30A.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.