Electrician Red Seal · Question
A technician is troubleshooting a three-phase motor control circuit. The motor hums but does not start when the START pushbutton is pressed, and the thermal overload relay is not tripped. A voltmeter across the motor terminals reads 240 V between L1-L2, L2-L3, and L1-L3. Which of the following is the MOST likely cause?
If the motor hums but doesn't start, it suggests that the motor is receiving power but cannot establish a rotating magnetic field, often due to a single-phasing
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A technician is troubleshooting a three-phase motor control circuit. The motor hums but does not start when the START pushbutton is pressed, and the thermal overload relay is not tripped. A voltmeter across the motor terminals reads 240 V between L1-L2, L2-L3, and L1-L3. Which of the following is the MOST likely cause?
Answer options:
- A welded contactor contact in one phase. ✅ An open circuit in one phase of the motor winding.
- Incorrect wiring of the START/STOP pushbuttons.
- A faulty auxiliary contact on the motor contactor.
Correct answer: An open circuit in one phase of the motor winding.
Explanation: If the motor hums but doesn't start, it suggests that the motor is receiving power but cannot establish a rotating magnetic field, often due to a single-phasing condition. An open circuit in one phase of the motor winding (or supply) would lead to 2 phases energized and one open, causing humming and no rotation. Welded contacts would prevent the motor from stopping, not starting. Pushbutton wiring or auxiliary contacts typically affect the control circuit, preventing contactor engagement rather than causing humming.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.