A programmable logic controller (PLC) is being used to control a series of pumps. The input module receives a 24 V DC signal from a pressure switch, and the output module actuates a 120 V AC contactor coil. What type of isolation is typically employed in the output module to protect the PLC's internal low-voltage electronics from the higher voltage of the contactor coil?
PLC output modules that connect to higher voltage/current loads like contactor coils typically use electrically isolated components to protect the sensitive int
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A programmable logic controller (PLC) is being used to control a series of pumps. The input module receives a 24 V DC signal from a pressure switch, and the output module actuates a 120 V AC contactor coil. What type of isolation is typically employed in the output module to protect the PLC's internal low-voltage electronics from the higher voltage of the contactor coil?
Answer options:
- Resistive isolation.
- Capacitive isolation. ✅ Relay (electromechanical) isolation or opto-isolation.
- Inductive isolation.
Correct answer: Relay (electromechanical) isolation or opto-isolation.
Explanation: PLC output modules that connect to higher voltage/current loads like contactor coils typically use electrically isolated components to protect the sensitive internal low-voltage logic circuitry. This is commonly achieved through either electromechanical relays (which provide physical separation) or opto-isolators (which use light to transmit signals across an insulating barrier), both effectively isolating the control voltage from the load voltage.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.