An industrial facility uses a 480 V, 3-phase ungrounded Delta system for motor loads. A maintenance electrician measures 277 V between phase A and ground, 277 V between phase B and ground, and 0 V between phase C and ground. What is the likely cause of these readings?

In an ungrounded Delta system, a single ground fault does not immediately cause an overcurrent device to trip. Instead, it places the faulted phase at ground po

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: An industrial facility uses a 480 V, 3-phase ungrounded Delta system for motor loads. A maintenance electrician measures 277 V between phase A and ground, 277 V between phase B and ground, and 0 V between phase C and ground. What is the likely cause of these readings?

Answer options:

  • A phase-to-phase fault. ✅ A ground fault on phase C.
  • An open phase conductor.
  • Improper bonding of the system.

Correct answer: A ground fault on phase C.

Explanation: In an ungrounded Delta system, a single ground fault does not immediately cause an overcurrent device to trip. Instead, it places the faulted phase at ground potential. The other two phases then present their phase-to-ground voltage, which for a 480V system is approximately 277V (480/√3) with respect to the faulted phase which is now at ground potential.

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

More about Electrician Red Seal

Related Questions

More for Electrician Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Electrician Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.