A welder's machine connected to a 240 V single-phase circuit has exposed metal parts that have become energized due to an internal insulation failure. The equipment grounding conductor (EGC) for the circuit is severed. What protective device would be MOST likely to trip or operate in this scenario, even without a complete EGC path, assuming the fault current is high enough?
A GFCI detects imbalances in current between the live and neutral conductors, indicating a leakage current to ground. Even with a severed EGC, a person touching
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A welder's machine connected to a 240 V single-phase circuit has exposed metal parts that have become energized due to an internal insulation failure. The equipment grounding conductor (EGC) for the circuit is severed. What protective device would be MOST likely to trip or operate in this scenario, even without a complete EGC path, assuming the fault current is high enough?
Answer options:
- A standard thermal-magnetic circuit breaker. ✅ A ground fault circuit interrupter (GFCI).
- A surge protective device (SPD).
- A residual current device with overcurrent protection (RCBO).
Correct answer: A ground fault circuit interrupter (GFCI).
Explanation: A GFCI detects imbalances in current between the live and neutral conductors, indicating a leakage current to ground. Even with a severed EGC, a person touching the energized metal could become the path to ground, causing the GFCI to trip. A standard breaker would only trip if the fault current directly returned to the source (phase-to-neutral or phase-to-ground via an intact EGC) at a high enough level.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.