Electrician Red Seal · Question
An industrial electrician is troubleshooting intermittent nuisance tripping of a ground fault circuit interrupter (GFCI) on a 120 V, 15 A circuit supplying a washdown pump in a wet location. After disconnecting the pump, the GFCI holds, but when the pump is connected, it trips almost immediately. A megohmmeter test between the pump's motor winding and its frame shows 0.8 MΩ. What is the most likely cause of the GFCI tripping?
A megohmmeter reading of 0.8 MΩ (800 kΩ) for a 120 V circuit indicates significant insulation degradation, allowing leakage current to flow from the winding to
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An industrial electrician is troubleshooting intermittent nuisance tripping of a ground fault circuit interrupter (GFCI) on a 120 V, 15 A circuit supplying a washdown pump in a wet location. After disconnecting the pump, the GFCI holds, but when the pump is connected, it trips almost immediately. A megohmmeter test between the pump's motor winding and its frame shows 0.8 MΩ. What is the most likely cause of the GFCI tripping?
Answer options:
- The GFCI is faulty and needs replacement.
- The neutral conductor is shared with another circuit. ✅ The motor winding insulation is degrading, causing leakage current to ground.
- The pump's power conductors are undersized for the motor load.
Correct answer: The motor winding insulation is degrading, causing leakage current to ground.
Explanation: A megohmmeter reading of 0.8 MΩ (800 kΩ) for a 120 V circuit indicates significant insulation degradation, allowing leakage current to flow from the winding to the motor's grounded frame. This leakage current, even if below the circuit breaker's trip rating, will be detected by the GFCI as an imbalance between the live and neutral conductors, causing it to trip. A healthy motor insulation should typically read in the millions of ohms.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.