Electrician Red Seal · Question
You are troubleshooting a 480 V, 3-phase motor that is running excessively hot. You measure the current in each phase and obtain 25 A, 28 A, and 35 A. The motor's nameplate FLC is 30 A. What is the most likely cause of the overheating?
The measured currents show a significant unbalance (10 A difference between the lowest and highest phase current), which can cause disproportionate heating in t
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: You are troubleshooting a 480 V, 3-phase motor that is running excessively hot. You measure the current in each phase and obtain 25 A, 28 A, and 35 A. The motor's nameplate FLC is 30 A. What is the most likely cause of the overheating?
Answer options: ✅ Unbalanced phase currents causing excessive losses.
- The motor is significantly overloaded.
- Loose connections in the motor termination box.
- High ambient temperature around the motor enclosure.
Correct answer: Unbalanced phase currents causing excessive losses.
Explanation: The measured currents show a significant unbalance (10 A difference between the lowest and highest phase current), which can cause disproportionate heating in the motor windings due to negative sequence currents. While the average current (29.3 A) is near FLC, the unbalance is the primary concern here. Overloading would typically show all three phases significantly above 30A. Loose connections might cause heating at the connection point rather than throughout the motor windings, and high ambient temperature would be a general factor, not specific to unbalanced current.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.