Electrician Red Seal · Question
A 120 V, single-phase motor in an industrial fan application makes a loud buzzing noise and trips its overcurrent device almost immediately when energized. You perform an insulation resistance test with a megohmmeter between the motor's line terminals and its frame, and read 0.5 MΩ. What is the most probable cause of the tripping?
A megohmmeter reading of 0.5 MΩ (500 kΩ) to ground is below the typical acceptable threshold of 1 MΩ for this voltage class, indicating weak or compromised insu
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 120 V, single-phase motor in an industrial fan application makes a loud buzzing noise and trips its overcurrent device almost immediately when energized. You perform an insulation resistance test with a megohmmeter between the motor's line terminals and its frame, and read 0.5 MΩ. What is the most probable cause of the tripping?
Answer options: ✅ A ground fault in the motor windings.
- The motor is severely overloaded.
- An open circuit in the motor windings.
- A faulty starting capacitor.
Correct answer: A ground fault in the motor windings.
Explanation: A megohmmeter reading of 0.5 MΩ (500 kΩ) to ground is below the typical acceptable threshold of 1 MΩ for this voltage class, indicating weak or compromised insulation. This suggests a ground fault, where current is leaking from the windings to the motor frame, causing the overcurrent device to trip. Overloading would generally not result in such a low insulation resistance reading to ground. An open circuit would prevent current flow, and a faulty starting capacitor would prevent the motor from starting but not typically cause an immediate trip due to a ground fault.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.