Electrician Red Seal · Question
A 575 V, three-phase induction motor is consistently tripping its overload relays after running for only a few minutes, even though the driven load seems normal. An amperage check shows currents of 25 A, 30 A, and 28 A on the three phases. The motor nameplate FLA is 28 A. What is the most likely cause of the tripping?
The current readings (25 A, 30 A, 28 A) show a significant unbalance (phase B is higher than the other two). Voltage unbalance can cause current unbalance, lead
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 575 V, three-phase induction motor is consistently tripping its overload relays after running for only a few minutes, even though the driven load seems normal. An amperage check shows currents of 25 A, 30 A, and 28 A on the three phases. The motor nameplate FLA is 28 A. What is the most likely cause of the tripping?
Answer options:
- The motor is significantly underloaded, causing regeneration. ✅ There is an unbalanced voltage supply to the motor.
- The overload heater elements are oversized.
- The motor bearings are worn out, causing mechanical drag.
Correct answer: There is an unbalanced voltage supply to the motor.
Explanation: The current readings (25 A, 30 A, 28 A) show a significant unbalance (phase B is higher than the other two). Voltage unbalance can cause current unbalance, leading to overheating in the motor windings, even if the average current is at or below FLA. This overheating will trip the overload relays.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.