A manufacturing plant has a main electrical feeder rated for 800 A at 600 V. Power factor correction has been installed, bringing the average power factor from 0.75 lagging to 0.95 lagging. With the improved power factor, how much more active power (in kW) can the feeder now supply without exceeding its current rating? Assume a three-phase system.
The maximum apparent power (S) the feeder can supply is √3 * V * I = √3 * 600 V * 800 A = 831,384 VA = 831.38 kVA. Initial active power P1 = S * PF1 = 831.38 kV
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A manufacturing plant has a main electrical feeder rated for 800 A at 600 V. Power factor correction has been installed, bringing the average power factor from 0.75 lagging to 0.95 lagging. With the improved power factor, how much more active power (in kW) can the feeder now supply without exceeding its current rating? Assume a three-phase system.
Answer options: ✅ 166.3 kW
- 83.3 kW
- 222.1 kW
- 138.8 kW
Correct answer: 166.3 kW
Explanation: The maximum apparent power (S) the feeder can supply is √3 * V * I = √3 * 600 V * 800 A = 831,384 VA = 831.38 kVA. Initial active power P1 = S * PF1 = 831.38 kVA * 0.75 = 623.53 kW. New active power P2 = S * PF2 = 831.38 kVA * 0.95 = 789.81 kW. The increase in active power is P2 - P1 = 789.81 kW - 623.53 kW = 166.28 kW. Option A (166.3 kW) is the closest.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.