An outlet box contains two #14/2 NMD-90 cables and one duplex receptacle. What is the minimum box volume required in millilitres (mL)?
Per CEC Rule 12-3034 and Table 23: two #14 AWG conductors from each cable (4 total) count as 4 x 24.6 mL = 98.4 mL. Both ground wires count as one largest condu
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: An outlet box contains two #14/2 NMD-90 cables and one duplex receptacle. What is the minimum box volume required in millilitres (mL)?
Answer options:
- 180 mL
- 213 mL ✅ 246 mL
- 295 mL
Correct answer: 246 mL
Explanation: Per CEC Rule 12-3034 and Table 23: two #14 AWG conductors from each cable (4 total) count as 4 x 24.6 mL = 98.4 mL. Both ground wires count as one largest conductor (1 x 24.6 mL). The duplex receptacle counts as two #14 AWG conductors (2 x 24.6 mL = 49.2 mL). Total = 98.4 + 24.6 + 49.2 + 49.2 (cable clamps) = 221.4 mL. A device box of 246 mL is the next standard size up.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.