A 3-phase, 4-wire, 120/208 V wye-connected system supplies a balanced non-linear load. Under which condition must the neutral conductor be counted as a current-carrying conductor for ampacity correction purposes?
CEC Rule 4-004(1)(d) states that the neutral conductor must be counted as a current-carrying conductor where a major portion of the load consists of non-linear
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: A 3-phase, 4-wire, 120/208 V wye-connected system supplies a balanced non-linear load. Under which condition must the neutral conductor be counted as a current-carrying conductor for ampacity correction purposes?
Answer options:
- It is never counted
- Only when the load is more than 50% of the circuit ampacity ✅ Always, when non-linear loads are present
- Only if the load is unbalanced by more than 10%
Correct answer: Always, when non-linear loads are present
Explanation: CEC Rule 4-004(1)(d) states that the neutral conductor must be counted as a current-carrying conductor where a major portion of the load consists of non-linear loads. Harmonics on these systems can cause significant neutral current, even when the phase currents are balanced.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.