A #2 AWG copper conductor with RW90 insulation is used in a circuit. According to CEC Table 2, what is its allowable ampacity when in a raceway with up to 3 conductors, assuming a termination temperature of 75°C?

Although RW90 insulation is rated for 90°C, the conductor's ampacity is limited by the termination temperature of the equipment, which is typically 75°C for dev

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: A #2 AWG copper conductor with RW90 insulation is used in a circuit. According to CEC Table 2, what is its allowable ampacity when in a raceway with up to 3 conductors, assuming a termination temperature of 75°C?

Answer options:

  • 95 A ✅ 115 A
  • 130 A
  • 175 A

Correct answer: 115 A

Explanation: Although RW90 insulation is rated for 90°C, the conductor's ampacity is limited by the termination temperature of the equipment, which is typically 75°C for devices over 100A (Rule 4-006). Therefore, you must use the 75°C column of Table 2, which gives an ampacity of 115 A for a #2 AWG copper conductor.