Expansion joints are required for straight runs of rigid PVC conduit to compensate for thermal expansion and contraction. At what approximate length change per 30m of conduit might one be needed for a 50°C temperature change?
According to CEC Appendix B on Rule 12-1114, PVC conduit changes length by approximately 6.8 mm for every 10°C change in temperature over a 10m length. A 50°C c
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
Question: Expansion joints are required for straight runs of rigid PVC conduit to compensate for thermal expansion and contraction. At what approximate length change per 30m of conduit might one be needed for a 50°C temperature change?
Answer options:
- 20 mm
- 50 mm ✅ 100 mm
- 150 mm
Correct answer: 100 mm
Explanation: According to CEC Appendix B on Rule 12-1114, PVC conduit changes length by approximately 6.8 mm for every 10°C change in temperature over a 10m length. A 50°C change over 30m results in a length change of (6.8 mm * (50/10) * (30/10)) = 102 mm. An expansion joint is required to accommodate this movement.
Start free practice for Electrician Red Seal
150 questions · no signup required · 40 free questions per day
More about Electrician Red Seal
Related Questions
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
- A Red Seal electrician is setting up temporary power for a construction site. The main temporary service is a
- A new industrial facility requires a 600 V, three-phase, 150 A feeder to supply a motor control centre. The co
More for Electrician Red Seal candidates
Practice tests
Question explanations
- A residential garage is to be wired with a 15 A, 120 V duplex receptacle. According to the Canadian Electrical
- During a renovation of a commercial kitchen, an electrician needs to replace an old single-phase, 240 V, 5 kW
- A commercial kitchen is being renovated, and several new 4 kW, 208 V, single-phase electric ovens are being in
- What is the minimum working space depth required in front of an electrical panel rated 200 A, 120/240 V, locat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Electrician Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.