According to the Canadian Electrical Code (CEC), what is the minimum acceptable clear working space in front of an electrical panel operating at 120/208V, when there are no live parts on the opposite side of the working space?

CEC Rule 2-308(1)(a) specifies a minimum clear working space of 750 mm for equipment operating at 0-150V to ground. While 120/208V is a multi-phase system, the

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: According to the Canadian Electrical Code (CEC), what is the minimum acceptable clear working space in front of an electrical panel operating at 120/208V, when there are no live parts on the opposite side of the working space?

Answer options: ✅ 750 mm (30 inches)

  • 900 mm (36 inches)
  • 1000 mm (39 inches)
  • 1200 mm (48 inches)

Correct answer: 750 mm (30 inches)

Explanation: CEC Rule 2-308(1)(a) specifies a minimum clear working space of 750 mm for equipment operating at 0-150V to ground. While 120/208V is a multi-phase system, the voltage to ground from any phase is 120V.