According to CEC Rule 12-904(3), what percentage of a rigid conduit's cross-sectional area can be occupied by conductors if there are more than two conductors (excluding bonding and neutral for a multi-wire circuit)?

CEC Rule 12-904(3) references Appendix B Table B4, which states that for three or more conductors in a conduit, the maximum fill is 40% of the conduit's cross-s

Start free practice for Electrician Red Seal

150 questions · no signup required · 40 free questions per day

Start Practice →

Question: According to CEC Rule 12-904(3), what percentage of a rigid conduit's cross-sectional area can be occupied by conductors if there are more than two conductors (excluding bonding and neutral for a multi-wire circuit)?

Answer options:

  • 30% ✅ 40%
  • 50%
  • 60%

Correct answer: 40%

Explanation: CEC Rule 12-904(3) references Appendix B Table B4, which states that for three or more conductors in a conduit, the maximum fill is 40% of the conduit's cross-sectional area. For two conductors, it's 31%, and for one, it's 53%.