A plumber is sizing a common vent for two water closets installed back-to-back in a commercial washroom. Each water closet has a drainage fixture unit (DFU) value of 6. If the common vent also serves a lavatory (2 DFU) located nearby on the same floor, what should be the minimum nominal pipe size for the common vent according to the NPC?

Each water closet has 6 DFUs, so two would be 12 DFUs. Adding the lavatory's 2 DFUs brings the total to 14 DFUs. According to NPC Table 2.5.7.1.(2) for a common

Start free practice for Plumber Red Seal

177 questions · no signup required · 40 free questions per day

Start Practice →

Question: A plumber is sizing a common vent for two water closets installed back-to-back in a commercial washroom. Each water closet has a drainage fixture unit (DFU) value of 6. If the common vent also serves a lavatory (2 DFU) located nearby on the same floor, what should be the minimum nominal pipe size for the common vent according to the NPC?

Answer options:

  • 50 mm
  • 65 mm ✅ 75 mm
  • 100 mm

Correct answer: 75 mm

Explanation: Each water closet has 6 DFUs, so two would be 12 DFUs. Adding the lavatory's 2 DFUs brings the total to 14 DFUs. According to NPC Table 2.5.7.1.(2) for a common vent, a vent pipe serving 14 DFUs requires a minimum nominal pipe size of 75 mm. Options 50 mm and 65 mm are too small for this DFU load.

Start free practice for Plumber Red Seal

177 questions · no signup required · 40 free questions per day

Start Practice →

More about Plumber Red Seal

Related Questions

More for Plumber Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Plumber Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.