A plumber is designing the venting system for a multi-story commercial building. A 100 mm soil or waste stack typically requires what minimum nominal pipe size for its stack vent, according to the NPC?
The National Plumbing Code of Canada generally requires that a stack vent, and any vent pipe that extends through the roof, is not less than 65 mm nominal pipe
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
Question: A plumber is designing the venting system for a multi-story commercial building. A 100 mm soil or waste stack typically requires what minimum nominal pipe size for its stack vent, according to the NPC?
Answer options:
- 38 mm
- 50 mm ✅ 65 mm
- 75 mm
Correct answer: 65 mm
Explanation: The National Plumbing Code of Canada generally requires that a stack vent, and any vent pipe that extends through the roof, is not less than 65 mm nominal pipe size where the soil or waste stack is 100 mm in size. This ensures adequate air circulation and prevents frost closure at the roof terminal.
Start free practice for Plumber Red Seal
177 questions · no signup required · 40 free questions per day
More about Plumber Red Seal
Related Questions
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
- A plumber is considering the velocity of water in a 50 mm (2") copper pipe supplying a commercial building. Ex
- A plumber is designing the domestic hot water recirculation system for a multi-story residential building. Wha
More for Plumber Red Seal candidates
Practice tests
Question explanations
- Before starting a new plumbing installation in a residential basement, what is the primary reason why a plumbe
- A plumber is installing a new kitchen sink in an existing residential dwelling. The sink drain is connected to
- A plumber is installing drainage for a dishwasher in a residential kitchen. The dishwasher P-trap is located 1
- A plumber is asked to install a backflow prevention assembly on a lawn irrigation system connected to the pota
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Plumber Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.