A hydronic heating system is installed in a building at an elevation of 100 metres above sea level. The boiler is located in the basement, 3 metres below the lowest heating terminal. What is the minimum cold fill pressure (static pressure) required at the boiler to ensure adequate pressure at the highest point of the system?

The minimum cold fill pressure must be sufficient to overcome the static head of the highest point in the system. For every 1 metre of height, approximately 10

Start free practice for Plumber Red Seal

177 questions · no signup required · 40 free questions per day

Start Practice →

Question: A hydronic heating system is installed in a building at an elevation of 100 metres above sea level. The boiler is located in the basement, 3 metres below the lowest heating terminal. What is the minimum cold fill pressure (static pressure) required at the boiler to ensure adequate pressure at the highest point of the system?

Answer options: ✅ 30 kPa (4.4 psi)

  • 60 kPa (8.7 psi)
  • 90 kPa (13.1 psi)
  • 120 kPa (17.4 psi)

Correct answer: 30 kPa (4.4 psi)

Explanation: The minimum cold fill pressure must be sufficient to overcome the static head of the highest point in the system. For every 1 metre of height, approximately 10 kPa of pressure is required. Therefore, for a 3-metre static head, a minimum of 30 kPa (3m x 10kPa/m = 30 kPa) is needed. This ensures water reaches the top of the system and provides a slight positive pressure to prevent air ingress.

Start free practice for Plumber Red Seal

177 questions · no signup required · 40 free questions per day

Start Practice →

More about Plumber Red Seal

Related Questions

More for Plumber Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Plumber Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.