A positive displacement compressor is operating with a suction pressure of 241 kPa (35 psig) and a discharge pressure of 1379 kPa (200 psig). If the suction line temperature is 10°C (50°F) and the corresponding saturated suction temperature for the refrigerant (R-404A) is -7°C (19°F), what is the superheat at the compressor inlet?
The superheat at the compressor inlet is the difference between the actual suction line temperature and the saturated suction temperature. So, 10°C - (-7°C) = 1
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
Question: A positive displacement compressor is operating with a suction pressure of 241 kPa (35 psig) and a discharge pressure of 1379 kPa (200 psig). If the suction line temperature is 10°C (50°F) and the corresponding saturated suction temperature for the refrigerant (R-404A) is -7°C (19°F), what is the superheat at the compressor inlet?
Answer options:
- 3°C (5.4°F)
- 10°C (18°F) ✅ 17°C (30.6°F)
- -7°C (-12.6°F)
Correct answer: 17°C (30.6°F)
Explanation: The superheat at the compressor inlet is the difference between the actual suction line temperature and the saturated suction temperature. So, 10°C - (-7°C) = 17°C.
Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal
500 questions · no signup required · 40 free questions per day
More about Refrigeration & Air Conditioning Mechanic Red Seal
Related Questions
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
- Which type of electric motor requires a capacitor for starting and running, offering higher efficiency and bet
- When evacuating a refrigeration system, what is the recommended deep vacuum level, typically measured in micro
More for Refrigeration & Air Conditioning Mechanic Red Seal candidates
FAQs
Question explanations
- Which of the following refrigerants is a hydrofluorocarbon (HFC) and has a high ozone depletion potential (ODP
- Which component is responsible for compressing the refrigerant vapour to a high pressure and temperature?
- According to the Canadian Electrical Code (CEC), what is the minimum required working clearance in front of el
- What is the main operating characteristic difference between a fixed orifice (capillary tube) and a Thermostat
Ready to practice?
Free, no signup required. Build a wrong-question list as you go.
Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →Related courses
Other Canadian certifications candidates often prepare for alongside this one.