A walk-in freezer using R-407C is exhibiting low suction pressure and high superheat at the evaporator outlet, but the compressor discharge temperature is also unusually low. What is the most probable cause of these symptoms?

A restricted liquid line or plugged filter drier reduces the amount of liquid refrigerant entering the evaporator, leading to low suction pressure, high superhe

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A walk-in freezer using R-407C is exhibiting low suction pressure and high superheat at the evaporator outlet, but the compressor discharge temperature is also unusually low. What is the most probable cause of these symptoms?

Answer options:

  • Overcharged refrigerant system
  • Non-condensable gases in the system
  • Dirty condenser coil ✅ Restricted liquid line or filter drier

Correct answer: Restricted liquid line or filter drier

Explanation: A restricted liquid line or plugged filter drier reduces the amount of liquid refrigerant entering the evaporator, leading to low suction pressure, high superheat, and often a reduced load on the compressor causing a lower discharge temperature.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.