A refrigeration system is experiencing high superheat at the compressor suction line and low suction pressure. The discharge pressure is normal, but the compressor is running continuously. Which of the following is the most likely cause?

A restricted liquid line filter-drier reduces refrigerant flow to the evaporator, resulting in low suction pressure and high superheat as the evaporator starves

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration system is experiencing high superheat at the compressor suction line and low suction pressure. The discharge pressure is normal, but the compressor is running continuously. Which of the following is the most likely cause?

Answer options:

  • Overcharged refrigerant system ✅ Restricted liquid line filter-drier
  • Condenser fan motor failure
  • Failed compressor suction valve

Correct answer: Restricted liquid line filter-drier

Explanation: A restricted liquid line filter-drier reduces refrigerant flow to the evaporator, resulting in low suction pressure and high superheat as the evaporator starves. The compressor continues to run trying to meet the cooling demand.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.