A rooftop HVAC unit is operating with high head pressure and low subcooling. The discharge line is very hot. What could be the cause?

Reversed condenser fan rotation significantly reduces airflow over the condenser, leading to poor heat rejection, high head pressure, and a very hot discharge l

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A rooftop HVAC unit is operating with high head pressure and low subcooling. The discharge line is very hot. What could be the cause?

Answer options:

  • Evaporator coil is deeply frosted ✅ Condenser fan motor has reversed rotation
  • Liquid line solenoid valve is stuck closed
  • Expansion valve is open too wide

Correct answer: Condenser fan motor has reversed rotation

Explanation: Reversed condenser fan rotation significantly reduces airflow over the condenser, leading to poor heat rejection, high head pressure, and a very hot discharge line. Low subcooling would also be observed due to inefficient condensation.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.