A refrigeration system with a nameplate charge of 15 kg of R-410A is being recovered. The recovery unit is rated for a maximum recovery rate of 0.5 kg/min. If the technician starts recovery at 10:00 AM and achieves 90% recovery before the system pressure equalizes, approximately what time would the initial recovery stage be completed?

The amount of refrigerant to recover is 15 kg * 0.90 = 13.5 kg. At a rate of 0.5 kg/min, the time required is 13.5 kg / 0.5 kg/min = 27 minutes. Therefore, the

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

Question: A refrigeration system with a nameplate charge of 15 kg of R-410A is being recovered. The recovery unit is rated for a maximum recovery rate of 0.5 kg/min. If the technician starts recovery at 10:00 AM and achieves 90% recovery before the system pressure equalizes, approximately what time would the initial recovery stage be completed?

Answer options: ✅ 10:27 AM

  • 10:30 AM
  • 10:20 AM
  • 10:45 AM

Correct answer: 10:27 AM

Explanation: The amount of refrigerant to recover is 15 kg * 0.90 = 13.5 kg. At a rate of 0.5 kg/min, the time required is 13.5 kg / 0.5 kg/min = 27 minutes. Therefore, the recovery would be completed around 10:27 AM, assuming a consistent recovery rate.

Start free practice for Refrigeration & Air Conditioning Mechanic Red Seal

500 questions · no signup required · 40 free questions per day

Start Practice →

More about Refrigeration & Air Conditioning Mechanic Red Seal

Related Questions

More for Refrigeration & Air Conditioning Mechanic Red Seal candidates

Ready to practice?

Free, no signup required. Build a wrong-question list as you go.

Start Free Refrigeration & Air Conditioning Mechanic Red Seal Practice →

Related courses

Other Canadian certifications candidates often prepare for alongside this one.